Can I tell what voltage this air compressor is set for?

Status
Not open for further replies.

Cannonmn

Member
Location
Northern va
15 hp 3-cyl recip air compressor by I.R. Line voltage wires are 10 gauge. Amps for various voltages shown on Motor plate. See wire colors. Is this evidence conclusive enough for you to tell me what voltage to hook up?

img_5659-e1500419413208.jpg


img_5666-e1500419459398.jpg
 
One can only assume it's 480.

Take the cover off the peckerhead and see how the leads are connected. That will be the tell.
 
15 hp 3-cyl recip air compressor by I.R. Line voltage wires are 10 gauge. Amps for various voltages shown on Motor plate. See wire colors. Is this evidence conclusive enough for you to tell me what voltage to hook up?

img_5659-e1500419413208.jpg


img_5666-e1500419459398.jpg
You can run 208 or 480 to the motor, you just need to make sure you wire the motor leads per the wiring diagram in the lower right corner of the nameplate for low or high voltage. I'm guessing it was previously wired 480v based on the wire colors Brown Orange Yellow and #10 isn't big enough for a 15HP motor at 208v and 40 amps FLC.
 
You can run 208 or 480 to the motor, you just need to make sure you wire the motor leads per the wiring diagram in the lower right corner of the nameplate for low or high voltage. I'm guessing it was previously wired 480v based on the wire colors Brown Orange Yellow and #10 isn't big enough for a 15HP motor at 208v and 40 amps FLC.


Thanks, just started unpacking it and hadn't recognized the diagrams, looked like decoration or something. I don't know much about this but I'll probably leave it wired at 480 v if proves to be that way now.
 
Last edited:
... hadn't recognized the diagrams, looked like decoration or something. ...
Please hire a qualified electrician.

-----------------------------------------------------

I am closing this thread, in accordance with the Forum rules. This Forum is intended to assist professional electricians, inspectors, engineers, and other members of the electrical industry in the performance of their job-related tasks. However, if you are not an electrician or an electrical contractor, then we are not permitted to help you perform your own electrical installation work.


If I have misjudged the situation, if for example this project is related to your work, then send me a Private Message. If you can show me that I am wrong, and that you are a licensed electrician (or at least a licensed apprentice), then I will reopen your post, and offer an apology for the delay and inconvenience.