Can I use a 220V 3-phase shredder on a 208V 3-phase portable generator?

Status
Not open for further replies.

kbsipin

New member
Location
Malde, MA USA
Hello!

I have a shredder with a nameplate that says: 220V 3-phase 60 Hz. I would like to be able to use this equipment via a portable generator. The one I am looking at is the Subaru RGV13100T - 10,000 Watt Electric Start Generator (208V - 3-Phase). Will it run my shredder?

Please help!

Thank you!!!
Ken
 
Hello!

I have a shredder with a nameplate that says: 220V 3-phase 60 Hz. I would like to be able to use this equipment via a portable generator. The one I am looking at is the Subaru RGV13100T - 10,000 Watt Electric Start Generator (208V - 3-Phase). Will it run my shredder?

Please help!

Thank you!!!
Ken
A shredder that needs 10kW? Must be a beast.
 
If it is 220V

If it is 220V

If it is 220 V on the nametag there should be no problem. generally a motor is ok with +/- %10 of rated voltage. So 220V motor is 22v up or down so 198-242v. Just make sure you check the frequency that is on the motor 220v three phase may be 50hz European.
 
If it is 220 V on the nametag there should be no problem. generally a motor is ok with +/- %10 of rated voltage. So 220V motor is 22v up or down so 198-242v. Just make sure you check the frequency that is on the motor 220v three phase may be 50hz European.
In which case the V/f ratio would be severely off (change in numerator and denominator would work in the same direction) leading to a significant decrease in motor torque and power.
 
If it is 220 V on the nametag there should be no problem. generally a motor is ok with +/- %10 of rated voltage. So 220V motor is 22v up or down so 198-242v. Just make sure you check the frequency that is on the motor 220v three phase may be 50hz European.
The OP stated that it was 60Hz on the nameplate.
 
Not sure what you mean by shredder, we have a machine we call a shredder: 480V, 150hp that we use to grind polyethylene. I have a paperless chart recorder monitoring the motor current (the reason is a whole other story) and the thing produces severe current spikes on a regular basis. You'll want to be sure everything is sized properly.
 
Not sure what you mean by shredder, we have a machine we call a shredder: 480V, 150hp that we use to grind polyethylene. I have a paperless chart recorder monitoring the motor current (the reason is a whole other story) and the thing produces severe current spikes on a regular basis. You'll want to be sure everything is sized properly.
Yes, shredder is a fairly generic term, there are some that probably make yours look small as well.
 
Yeah they had a 400 hp in the warehouse when we looked at ours. Terrifying.

could be a car shredder or tub grinder, but those typically have 600-800HP engines powering them, not electric motors. Maybe this is a cardboard shredder or large (mobile) paper shredder. 10kw genset isnt going to tolerate jams and subsequent current spikes too well, unless the machine has auto reverse/auto shutdown/etc.
 