I'm installing a subpanel. The terminals in the service panel supplying the panel are rated 75C, the terminals in the panel are rated 75C, and I'll be using THHN copper conductors which are rated at 90C. Based on Table 310.15(B)(16) (NEC 2011), I'm planning to have a 90A breaker in the service panel, a 90A breaker in the sub, and I'll use 3 AWG THHN conductors between the panel.
A coworker pointed out that according to 240.4(B), I can use 4 AWG THHN instead of #3.
Can I really use #4 and a 90A breaker in this situation?