Here is the deal,
I have 3 transformers 480-240/120 Delta to Delta.
Main board is 1200A 480/277 Wye. Breakers are each 400A 480V (not 480/277V, actually i beleive they are rate to 600V anyway).
Q: can i connect from 480V Wye source to 480V Delta incoming at a transformer above directly? Voltages work, i was just going to skip N at first and add N to 240/120V delta outgoing as center tap.
Our main loads will be 240V 1ph (we'll balance them in subpanels), the 120V is only for service outlets (no permanent draw).
All equipment is in place already.
Thanks for the help !