Can I use NM cable NEC 300.22 ?

Status
Not open for further replies.

stevenj

Member
NEC 300.22 Wiring Question.
NEC 300.22 C execption ( wiring though ) Can NM cable be used for wire though?

HVAC supply air duct, quite large 11x 21 in dropped ceiling hallway. Could I use NM Cable for the runs that go above and alongside the supply duct? The NM would be fastened in the standard way to the joists. The joists are above the duct, and standard 2x4 inside walls.

300.22 states wiring installed in duct or plenums, anyplace where it says around the duct. I notice 300.22 states chamber. Does this count as a chamber ? I have 6-8 inches on either side of the duct and 2x8 joists above or am I reading this wrong.

I’m take It I only can use MC IMC MI, EMT,etc. and not NM cable at all.



Also The supply duct sets on 2x4 ‘s over a hall ceiling that will be rocked. I need to put fixtures on these 2x4’s i.e., 1.5 boxes would NM ok, as this would be below the supply air duct on the 2x4 with a steel box.

So My general question is can NM be used all.
 
Since the air will only be moving inside of the ducts your installation does not fall under 300.22(C). Since this is a dwelling the NM is permitted above the hung ceiling. You're good to go.
 
Since the air will only be moving inside of the ducts your installation does not fall under 300.22(C). Since this is a dwelling the NM is permitted above the hung ceiling. You're good to go.

Than you for the clarification on this . I was not sure if 300.22 or exception (c) applied to a dwelling.

thanks .
 