Can I wire two lamps with a four lamps ballast?

zappy

Senior Member
Location
CA.
All we have available are these four lamp T5 ballast. I was wondering if I could wire two lamps with it or do I need a two lamp ballast. Thank you for your help.
 

Attachments

  • IMG_9443.jpeg
    IMG_9443.jpeg
    563.7 KB · Views: 28

4-20mA

an analog man in a digital world
Location
Charleston SC
Occupation
Instrumentation & Electrical
Yes, but it doesn't show if you could wire it for two lamps so I guess you can't.
Huh? Looks like you could just use half of it and cap off what you don't use.... hopefully you're only asking for "code purposes"... is it against code? I have no idea, but this isn't exactly a brainteaser, wire-wise...
 

zappy

Senior Member
Location
CA.
Huh? Looks like you could just use half of it and cap off what you don't use.... hopefully you're only asking for "code purposes"... is it against code? I have no idea, but this isn't exactly a brainteaser, wire-wise...
I just assumed, because it didn't show two lamps but I did what you said. Thank you.
 

zappy

Senior Member
Location
CA.
Here's the old one. Is there anyway to test this with a meter to see if this ballast is bad?
 

Attachments

  • IMG_9444.jpeg
    IMG_9444.jpeg
    533.3 KB · Views: 6

4-20mA

an analog man in a digital world
Location
Charleston SC
Occupation
Instrumentation & Electrical
Here's the old one. Is there anyway to test this with a meter to see if this ballast is bad?
I'm not sure how to test one per se, never tried. I have read that some ballasts can produce over 600v and a lot of meters will not like that. Just from a quick Google search.
How's it smell? Usually, one can tell if they're fried like that.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Known good lamps, wiring correct, power present, lamps don't light = bad ballast

Ballast usually list the number of lamp combinations and the wiring diagram, if you try to wire them for more or less lamps than it's designed for, you either shorten the life of the ballast or the lamps.
 

kec

Senior Member
Location
CT
Occupation
Electrical Contractor
All we have available are these four lamp T5 ballast. I was wondering if I could wire two lamps with it or do I need a two lamp ballast. Thank you for your help.
Of course, just cap off single lamp on diagram.
 

zappy

Senior Member
Location
CA.
Huh? Looks like you could just use half of it and cap off what you don't use.... hopefully you're only asking for "code purposes"... is it against code? I have no idea, but this isn't exactly a brainteaser, wire-wise...
So I did like you said, and one fixture works fine. I took another new ballast to the next fixture that wasn't working, wired it up the same way, installed two new bulbs, and when I twist the bulbs, the lights comes on for a second and shuts off. Any ideas? i'm gonna take that new ballast down and install another new ballast to see what happens.
 

zappy

Senior Member
Location
CA.
So I did like you said, and one fixture works fine. I took another new ballast to the next fixture that wasn't working, wired it up the same way, installed two new bulbs, and when I twist the bulbs, the lights comes on for a second and shuts off. Any ideas? i'm gonna take that new ballast down and install another new ballast to see what happens.
I swapped the new ballast, and put in another new ballast, and now it works, so it's a bad ballast from the factory. 🙄
 

Flicker Index

Senior Member
Location
Pac NW
Occupation
Lights
The ballast will tell you the number of lamps and how to wire them.
Not always. Even if the label does not say so, the detailed specifications quite often allow more load variety.
Generally, operating fewer lamps result in elevated output on the remaining lamps.
 