Can I

Merry Christmas

JohnTheHeaterGuy

New User
Location
Hamilton
Occupation
Engineer/Manufacturers Rep
I have an application where I want to control a 3 element 480V screwplug heater with a line duty DPST thermostat. The thermostat is rated for 277V. If I wire the elements in WYE, this means that each connection of the thermostat will see 277V - even though there are 480V across the two poles - the latter point is what is giving me an allergic reaction (and my manager too). Being a mechanical engineer, I know enough to be dangerous, so that's why I've joined the forum, so I can ask the experts to point me in the right direction. Has anybody seen this application before and if so, where would I be able to get the confirmation that this is acceptable.
thanks if advance for your input.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I am allowing this post to collect design information, on the assumption that the actual installation will be done by a licensed electrician, whose input will also be obtained.
 

garbo

Senior Member
I am allowing this post to collect design information, on the assumption that the actual installation will be done by a licensed electrician, whose input will also be obtained.
Thanks for your commitment. I'm a second generation electrician that would give advice to friends & coworkers up to a point. Had a few co-workers who flipped houses and started doing own electrical work including replacing services then got mad when inspector failed them. I laughed when they wanted me to sell my soul ( pull an electrical permit ) and do drawings on how to do electrical work. Nope.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I say yes if the 480 is a solidly grounded wye source and the common point of the heaters goes back to that neutral.

There might be some issues with spacing of the thermostat contacts.

Otherwise no.
 