BMacky

Senior Member
Location
Foster City, CA
I've just roughed in a master bathroom and provided a couple of wall receptalces, one for each basin at the backsplash and within the 3-foot required spacing. The homeowner would like to eliminate the left hand side outlet and move the right-hand side outlet to the right, out of a mosaic tile pattern (which I was not made aware of until after the rough).

If I move the right side outlet to the preferred location, the left hand basin edge is over 3-feet from the outlet by a couple of inches. I will probably consult with the AHJ on this, but does anyone know if a listed medicine (Robern) cab with a GFCI-protected receptacle will cover me as far as the required receptacle goes for the left-hand basin?

Thanks!

Bob
 
The code just requires a receptacle within 3 feet of the basin, not withing 3 feet of all points on the basin. You're fine with one.

Mark

Edited: Sorry. Didn't see that there were 2 basins. I retract that answer. I would ask the AHJ.
 
BMacky said:
does anyone know if a listed medicine (Robern) cab with a GFCI-protected receptacle will cover me as far as the required receptacle goes for the left-hand basin?

Thanks!

Bob

IMSO it will not be compliant.

210.52(D)

The receptacle outlet shall be located on a wall or partition that is adjacent to the basin or basin countertop.
 
Can you take advantage of the exception to 210.52(D)? Is there a cabinet under each basin?
 
BMacky said:
but does anyone know if a listed medicine (Robern) cab with a GFCI-protected receptacle will cover me as far as the required receptacle goes for the left-hand basin?
Thanks! Bob

NO!

210.52 Dwelling Unit Receptacle Outlets.
This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. Receptacle outlets required by this section shall be in addition to any receptacle that is part of a luminaire (lighting fixture) or appliance, located within cabinets or cupboards, or located more than 1.7 m (5? ft) above the floor.
 
jwelectric said:
NO!

210.52 Dwelling Unit Receptacle Outlets.
This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. Receptacle outlets required by this section shall be in addition to any receptacle that is part of a luminaire (lighting fixture) or appliance, located within cabinets or cupboards, or located more than 1.7 m (5? ft) above the floor.


This is the "dealbreaker" that most people seem not to see when they are reading the NEC.
That is why I teach the guys to read the section number as well as the subsection, looking for any exception that may follow.
 
I'm not sure I understand your point, Pierre. Are you agreeing or disagreeing with Mike?
 
jwelectric said:
210.52 Dwelling Unit Receptacle Outlets.

This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. Receptacle outlets required by this section shall be in addition to any receptacle that is part of a luminaire (lighting fixture) or appliance, located within cabinets or cupboards, or located more than 1.7 m (5? ft) above the floor.
The exception to 210.52(D) allows the "required" receptacle outlet on, but not inside, the basin cabinet, only. The NEC Handbook adds this commentary between 210.52(D) and 210.52(D) Exception:
This receptacle is required in addition to any receptacle that may be part of any luminaire or medicine cabinet.
 
I'm not sure Bmacky and busman are on the same page.

It sounds like busman thinks there is a receptacle within 3' of both basins without the medicine cabinet outlet.

I think Bmacky said the receptacle wasn't within 3' of the left-hand basin, and I think Busman took that to mean it wasn't within 3' of the left-hand EDGE of the basin.

Steve
 