Can multiple single lugs on a secondary side of a transformer, be bolted together?

Status
Not open for further replies.

RobbieR

Member
Location
Atlanta
I'm reviewing a field photo from the inside of a transformer. The secondary terminal points have (2) single barrel lugs bolted on top of each other for each phase. Is this allowed? It just doesn't seem right to me, but I can't find anything in the Code to probibit it unless I go to 110.3(B). I don't think these lugs are listed or labeled to be bolted on top of other lugs. I thought that's what mulitple-barrel lugs were for?
 

tkb

Senior Member
Location
MA
I wouldn't worry about it.
It is done that way every day and has been since Thomas Edison was a pup.

I don't know of anything that prohibits this practice.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
As long as the same amount of surface area still maintains contact I don't see a problem. Quite often you have no choice but to stack them.
 

TimK

Member
Location
Tacoma, WA
surface area

surface area

I'm reviewing a field photo from the inside of a transformer. The secondary terminal points have (2) single barrel lugs bolted on top of each other for each phase. Is this allowed? It just doesn't seem right to me, but I can't find anything in the Code to probibit it unless I go to 110.3(B). I don't think these lugs are listed or labeled to be bolted on top of other lugs. I thought that's what mulitple-barrel lugs were for?

Brings up a good question though, would the bottem one need twice the surface area in order to carry the ampacitiy of the second one in addition to its own?
 