ElectricPersonality
Member
- Location
- Philadelphia, PA
I would like to have a transformer located inside a school building feed two panels located in two outdoor trailers. If an enclosed circuit breaker was installed within 10' (secondary length) of the transformer on the secondary side, would it be permissable to install a wireway on the load side of the enclosed breaker and tap off two sets of conductors, one set for the first panelboard and the other set for the other panelboard (i.e. would 240.21 (B)(5) apply in this situation?).
I would like to avoid having to install a panelboard fed from the secondary of the transformer just to feed two more panelboards.