Can SER Cable be ran from main panel to attached garage 90 feet away?

Status
Not open for further replies.

x27

Member
Location
Ny
Occupation
Maintenance
Making sure I can use SER cable from the house panel through the drop ceiling to the subpanel in garage. If I remember there isn't a limit inside the house for ser but wasn't sure. Thank you.
 
Awesome. And the next question is about the 10 feet inside the garage to the actual subpanel. The cable will be run surface mounted on a 2 by4 wall but be sleeved in pipe and boxed out. Is that ok? It will be about 6.5 feet above finished floor
 
Making sure I can use SER cable from the house panel through the drop ceiling to the subpanel in garage. If I remember there isn't a limit inside the house for ser but wasn't sure. Thank you.
Limit on length is when used as the service entrance conductors. This limit is for all wiring methods presuming they are allowed to be used for service conductors, a few are not, NM cable would be one of them. NM however could be used for your particular garage feeder if it remains indoors the entire length. I'm guessing you maybe want an SE type cable because it should cost less if it has aluminum conductors, if copper is what you want either is fine.
 
Limit on length is when used as the service entrance conductors. This limit is for all wiring methods presuming they are allowed to be used for service conductors, a few are not, NM cable would be one of them. NM however could be used for your particular garage feeder if it remains indoors the entire length. I'm guessing you maybe want an SE type cable because it should cost less if it has aluminum conductors, if copper is what you want either is fine.
isn't that length limitation on USER cable?
 