Greetings,
I am at a loss (and my local building department is no better off) to find information related to derating multiple HVAC (typical hotel window/wall units rated 9,000 BTU [2.64 kilowatts] each). There are 72 rooms with two rooms per 30 amp, 208 VAC breaker and each breaker carrying a maximum of 25.4 amps on #10 THWN-2 wire derated to 70%, or 28 amps. As I have 36 breakers at 25.4 amps maximum each, there is a potential draw of 914 amps of power at 208 VAC if every unit was turned to the maximum rating. As this is never likely to be the case, I am certain there must be a table that tells me how much I can derate. Table 220.84 almost makes sense, as it would derate 62 or more units to a 23% demand factor, which is 210 amps, a much more workable number from distribution and load center standards.
Would anyone who has experience loading hotel HVAC units onto panels please send me in the proper direction? My building department thinks I should be using Table 220.44, but I feel as though that formula is way too liberal, requiring 481 amps of power for these units.
Regards - Baran
I am at a loss (and my local building department is no better off) to find information related to derating multiple HVAC (typical hotel window/wall units rated 9,000 BTU [2.64 kilowatts] each). There are 72 rooms with two rooms per 30 amp, 208 VAC breaker and each breaker carrying a maximum of 25.4 amps on #10 THWN-2 wire derated to 70%, or 28 amps. As I have 36 breakers at 25.4 amps maximum each, there is a potential draw of 914 amps of power at 208 VAC if every unit was turned to the maximum rating. As this is never likely to be the case, I am certain there must be a table that tells me how much I can derate. Table 220.84 almost makes sense, as it would derate 62 or more units to a 23% demand factor, which is 210 amps, a much more workable number from distribution and load center standards.
Would anyone who has experience loading hotel HVAC units onto panels please send me in the proper direction? My building department thinks I should be using Table 220.44, but I feel as though that formula is way too liberal, requiring 481 amps of power for these units.
Regards - Baran