The facility has a fusible safety switch outside the building mounted on the wall. Those 1000 amp fuses serve a panel in the building with a 1000 amp breaker. The trip unit is 1000A LSG. The contacts inside the breaker have burned up. The contacts were cleaned up a little and the three phase service was restored.
The company is in a time crunch for delivery of a replacement breaker. If the 1000 amp fuses serve as the main, why is the 1000 amp breaker required?
Can the panel be converted to lugs only and eliminate the breaker? I have not been to the location. I was asked to help locate the replacement breaker. Are the breaker contacts replaceable? The housing does not appear to be damaged.