Hello All,
The transformer is 112.5kVA 480-208V Delta-Wye 3 phase. It's above the fan-ventilated ceiling. The OCPDs on the primary and secondary are from the readily accessible panels on the floor. I don't think it violates section 450.13(B) because this is an attic (not a hollow space) with light, fan, catwalk and about 6.5' vertical clearance. Will an accessible 'door' required for this transformer and if yes, what size is that door and will a permanent ladder is required?
Thanks a lot.
The transformer is 112.5kVA 480-208V Delta-Wye 3 phase. It's above the fan-ventilated ceiling. The OCPDs on the primary and secondary are from the readily accessible panels on the floor. I don't think it violates section 450.13(B) because this is an attic (not a hollow space) with light, fan, catwalk and about 6.5' vertical clearance. Will an accessible 'door' required for this transformer and if yes, what size is that door and will a permanent ladder is required?