Re: Can this be real?

I saw this in a power engneering class I took a few years ago. My instructor said they were testing a switch w/o opening the breaker first. So this can happen under the right conditions. He had mulitiple diffrent videos of this type of arc from lots of high voltage equipment.
 

beanland

Senior Member
Location
Vancouver, WA
Re: Can this be real?

Movie is valid. Current is only the excitation current going down a high voltage power line, no load on the line. Capacitive coupling to ground is enough to cause this current. It may only be on the order of 3-10 Amperes. Looks like a 230-500kV line.
 

EEPeder

Member
Re: Can this be real?

I can confirm validity ... this picture is from my utility, it's 500kv on a very long line. This particular disconnect uses several lower voltage 'interrupter' units in series to break the arc of the line charging current. One of the interrupter units had failed and the remaining interrupter was unable to break full voltage so the external arc occurred repeatedly on operation until someone got a clue and figured out what was going on...
 