I'm having a pool / spa installed. Due to my wide driveway, I plan to run the main feeder (100A) to the pool panel / power center (AquaLink) from my meter service entrance panel, up into and across my (attached) garage attic, down the opposite exterior wall, and then LB down into a short run of buried PVC conduit over to the pool pump / heater skid. My electrician has proposed using Tray Cable.
Per NEC 2023, 336.10(9):
My application has only power conductors; no control circuits. Does that prohibit me from using TC-ER-JP cable as I describe above? Or is this simply poorly worded, and therefore TC-ER-JP cables containing solely power conductors are allowed (i.e., without a raceway in my attic)? I see no reason why the absence of control circuitry in the cable would somehow yield an inferior installation in terms of safety.
Per NEC 2023, 336.10(9):
Type TC-ER-JP cable containing conductors for both power and control circuits shall be permitted for branch circuits and feeders. Type TC-ER-JP cable used as interior wiring shall be installed per the requirements of Part II of Article 334 and, where installed as exterior wiring, shall be installed per the requirements of Part II of Article 340.
My application has only power conductors; no control circuits. Does that prohibit me from using TC-ER-JP cable as I describe above? Or is this simply poorly worded, and therefore TC-ER-JP cables containing solely power conductors are allowed (i.e., without a raceway in my attic)? I see no reason why the absence of control circuitry in the cable would somehow yield an inferior installation in terms of safety.