A proper handle tie is present. The 30-amp circuit handle ties spans across the breakers.
T tonype Senior Member Location New Jersey Feb 10, 2024 #1 A proper handle tie is present. The 30-amp circuit handle ties spans across the breakers.
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Feb 10, 2024 #2 Yes.
Little Bill Moderator Staff member Location Tennessee NEC:2017 Occupation Semi-Retired Electrician Feb 10, 2024 #3 Looks like a quad breaker. The inner 30A are common trip, the outer 15A are not. Very common in mobile homes.
Looks like a quad breaker. The inner 30A are common trip, the outer 15A are not. Very common in mobile homes.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Feb 10, 2024 #4 Can they? They pretty much have to, except for breakers like QO.
Little Bill Moderator Staff member Location Tennessee NEC:2017 Occupation Semi-Retired Electrician Feb 10, 2024 #6 tonype said: Click to expand... If I may ask, do you do home inspections as a PE?