My question is this, can standard 1 5/8” unistrut (Unistrut P1000T) be classified specifically as cable tray Under article 392, and not a strut type raceway as listed in 384?
I have a vendor that is trying to use slotted strut ascable tray for routing 6 triad 16awg control cables and 1 single pair 16awg. The full calculation comes out at 40.6% and he believes he is covered under 392.22 allowing 50% fill rather than the 40% fill and cover requirements for 384 raceway designation
I have a vendor that is trying to use slotted strut ascable tray for routing 6 triad 16awg control cables and 1 single pair 16awg. The full calculation comes out at 40.6% and he believes he is covered under 392.22 allowing 50% fill rather than the 40% fill and cover requirements for 384 raceway designation