JPing
Member
- Location
- Denver, CO
Forgive me if this has already been answered. I'm new to the forum and couldn't find anything while searching.
My situation is this:
I have a 150HP motor currently, that MAY be upgraded in the near to future to 300HP. As such I am designing the system to currently service the 150HP load, but by spending as little $$ as possible prepare for the 300HP motor. As such, my system looks like this:
600A
^
----o o-----| 300HP Harmonic Filter |-------| 300HP VFD |----- 150HP MTR
The cable from the 600A breaker thru the filter and to the VFD is sized for the 300HP load. However to save cost now I would like to size the cable from the VFD to the Motor for the 150HP load (as it is about 300 feet of cable).
The VFD comes with input fuses sized for 300HP (500A).
Here is the question: Is it permissible to use the current limiting features in the VFD to protect my "undersized" wiring between the VFD and the motor.
Note: I know that I can swap out the 400A fuses in the VFD with 225A or 250A fuses, but I still would like to look into the simpler "electronic" method.
Second question. Should my main breaker (the 600A) be a circuit breaker or a Motor Circuit Protector (MCP)?
You help is greatly appreciated.
My situation is this:
I have a 150HP motor currently, that MAY be upgraded in the near to future to 300HP. As such I am designing the system to currently service the 150HP load, but by spending as little $$ as possible prepare for the 300HP motor. As such, my system looks like this:
600A
^
----o o-----| 300HP Harmonic Filter |-------| 300HP VFD |----- 150HP MTR
The cable from the 600A breaker thru the filter and to the VFD is sized for the 300HP load. However to save cost now I would like to size the cable from the VFD to the Motor for the 150HP load (as it is about 300 feet of cable).
The VFD comes with input fuses sized for 300HP (500A).
Here is the question: Is it permissible to use the current limiting features in the VFD to protect my "undersized" wiring between the VFD and the motor.
Note: I know that I can swap out the 400A fuses in the VFD with 225A or 250A fuses, but I still would like to look into the simpler "electronic" method.
Second question. Should my main breaker (the 600A) be a circuit breaker or a Motor Circuit Protector (MCP)?
You help is greatly appreciated.