I would think yes. SF DBI may or may not still educating on PCS, but I'd be they're familiar with it by now. It's been in the code for nearly two years.
You can install 60A breker as well Provided that the Powerwall 3 is configured for panel limit Feature. Tesla site cts are installed to monitor the service conductors and 160A is kept as PCS panel limit setting. That means at the instant when the grid plus inveretr current exceeds 160A then powerwall will cut off the inverter production to stay within the limit of 160A.