Re: Can woes
I will write it tonight!
I will write it tonight!
Is there an installation/use standard for the IC-rated QL1QP 6" recessed can? I recently had an experience where the thermal sensor malfunctioned, melted through it's insulation and shorted itself to the can casing. I am trying to isolate what went wrong, and am attempting to eliminate the way we install the cans and trims.
The trim in question was an RM30WOV, with a 65W R-30 lamp installed. The excessive heat allowed by the defective thermal sensor melted the informational label on the interior of the can housing, and deformed the trim.
The can was installed in a cellulose-insulated ceiling.
I appreciate your attention to this matter.
George Stolz
Residential Electrician
Well, we were barking up the right tree. I just got off the phone with a rep with Capri, and he stated that the listing is only good for the plate in it's shipped location. It is adjustable for other can trims such as shower trims, which use a lower wattage bulb and have to be adjusted to work.Originally posted by davedottcom:
1)The stops are the reason the can is IC listed.
2)The space above the bulb at the IC "stop" level IS the difference in heat decipation.
3)The can's design "Allows" the bulb to be pushed up past the "stop" level but only for Non-IC situations.
4)If you have these "Pushed up bulbs" installed & buried under insulation, removing the insulation should make it a non-IC situation again.
...Originally posted by georgestolz:
As for the thermal sensor, ...Given the nature of what would occur when the thermal sensors insulation melted, a recall probably wasn't really necessary. The compromised sensor would ground itself out to the can housing, requiring the replacement of the can.