can you have 110&220v on the same outlet box?
Define what you mean by outlet box. If you're talking about a duplex receptacle the answer is yes but let me qualify that answer. You can install a 14/3 or 12/3 cable to a receptacle and snap off the tab on the phase side of the receptacle separating both hot legs and sharing the neutral. Now, although you have 240 volts existing at the junction box you actually have two, 120 volt circuits at the duplex receptacle. However, what you must do is feed that junction box from a 2-pole circuit breaker. That way, if someone has to work on that receptacle both phases can be shut off at once.

Now, what you cannot do is feed the receptacle in the same way as aforementioned and snap off the neutral tab instead of the phase tab and then feed the top half of the receptacle with 120 volts (hot and neutral) and the bottom half with 240 volts (hot-phase-1 and hot-phase-2).
a) the receptacle is not rated for that voltage or configuration
b) I don't know of any appliance that would be manufactured with a 15 or 20 amp, 120 volt plug and made to operate at 240 volts.

I'll defer to my colleagues for the code references.
 
Re: can you have?

Seems to me that any 4-wire outlet, such as for electric dryer, has exacltly that. So the answer is true.

Bob
 
Re: can you have?

404.8(B) - provides one instance where devices connected with certain voltages between them are restricted in there grouping. However this section applies to 120V with 277V.
 
Re: can you have?

In addition to Bthielen's post, here is a picture of single yoke device that would serve
an individual 125 v connection as well as an individual 240 v connection.

HBL5292_diagram.jpg


Roger
 
Re: can you have?

Wow ! Can't say that I've ever seen one of those so I stand corrected. That's what I like about this forum. Somebody's always willing to help you put your foot in your mouth with the help of a shoe horn !!
 
Re: can you have?

I have exactly that set up in my kitchen where I use a 240V electric kettle (bought from another country) on the countertop. Boils water MUCH faster than the stovetop, and as for 110V kettles well you needen't bother.
 
Re: can you have?

How is this puppy being fed?

With a DP 15Amp breaker?

two hots for the 240 and a continuous tab for the 120 hot and a neutral for the other side?

I would assume so.
 
Re: can you have?

Originally posted by Edward 99:
How is this puppy being fed?

With a DP 15Amp breaker?

two hots for the 240 and a continuous tab for the 120 hot and a neutral for the other side?

I would assume so.
Another option: a 2-pole breaker and a single-pole breaker side-by-side with a 3-pole handle-tie.

Wait a minute: That would require prying off the original 2-pole handle tie; wouldn't that be illegal?

I guess a 3-pole would be just as good. 3 single-poles wouldn't meet the "internal-trip" requirement for the 250v half.
 
Re: can you have?

Originally posted by georgestolz:
Originally posted by LarryFine:
3 single-poles wouldn't meet the "internal-trip" requirement for the 250v half.
Where is there a common trip requirement? :confused:
Let's see...
There's 210.4(C)Exc. 2. (210.7(C) requires the handle-tie.) I suppose one could argue that 240.20(B)(2) counters 210.4(C)Exc.2.

I've always been under the impression that, while handle-ties are acceptable for common manual breaker operation, an internal common-trip mechanism is required for overcurrent operation.
 
Re: can you have?

Originally posted by Edward 99:
How is this puppy being fed?

With a DP 15Amp breaker?

two hots for the 240 and a continuous tab for the 120 hot and a neutral for the other side?

I would assume so.
I would feed it with 3 wire, that would be two hots and a neutral.

This is a very common set up for window AC units or through wall AC units.
:)
 
Re: can you have?

I took a closer look at mine. 240V is fed by a DP 20A directly to the outlet - dedicated circuit. The 115V is fed from a circuit that has multiple recepticles and is GFCI protected at the loadcenter. EGC are separate for each outlet. There is no common wiring for either outlet of the duplex recepticle. I do vaguely recall a label applied to the face plate - it may have said something about separate feeds and 240V outlet, it's been a while.
 
Re: can you have?

Here is a diagram of one wiring option for the device from the Handbook. This diagram is also in manufactures wiring diagrams.

This was originally posted by Iwire in an earlier thread.

MWBC120240.JPG



Roger
 
Re: can you have?

Ann, no your set up is not incorrect, I was just showing the one option above. The device can be served with individual 120v and 240v circuits. as yours is, but it would have to comply with 210.7(C).

Roger
 