Define what you mean by outlet box. If you're talking about a duplex receptacle the answer is yes but let me qualify that answer. You can install a 14/3 or 12/3 cable to a receptacle and snap off the tab on the phase side of the receptacle separating both hot legs and sharing the neutral. Now, although you have 240 volts existing at the junction box you actually have two, 120 volt circuits at the duplex receptacle. However, what you must do is feed that junction box from a 2-pole circuit breaker. That way, if someone has to work on that receptacle both phases can be shut off at once.can you have 110&220v on the same outlet box?
Another option: a 2-pole breaker and a single-pole breaker side-by-side with a 3-pole handle-tie.Originally posted by Edward 99:
How is this puppy being fed?
With a DP 15Amp breaker?
two hots for the 240 and a continuous tab for the 120 hot and a neutral for the other side?
I would assume so.
Where is there a common trip requirement?Originally posted by LarryFine:
3 single-poles wouldn't meet the "internal-trip" requirement for the 250v half.
Let's see...Originally posted by georgestolz:
Where is there a common trip requirement?Originally posted by LarryFine:
3 single-poles wouldn't meet the "internal-trip" requirement for the 250v half.![]()
I would feed it with 3 wire, that would be two hots and a neutral.Originally posted by Edward 99:
How is this puppy being fed?
With a DP 15Amp breaker?
two hots for the 240 and a continuous tab for the 120 hot and a neutral for the other side?
I would assume so.