If I have a 200-A panel, can I run 200 amps continuously through it? Or can I run up to 160 A (= 200 A * 0.80)?
I think not. Here's my research:
In case I'm correct, I've just answered my own question. But I'm asking for you to check if I'm correct. Thanks in advance!
I think not. Here's my research:
- As we know, most breakers are not rated for 100% operation, and therefore should not have a load greater than 80% of its capacity (or equivalently, the breaker should have a capacity of at least 125% of the load) [art. 215.3 of 2020 NEC]. For example, we can't use a 200-A breaker if the continuous load will be/is 200 A, but we can either install the 200-A breaker and limit the load to 160 A (= 200 A*0.80), or better install a 250-A breaker (= 200 A * 1.25) without limiting the load. This applies for both the branch and the main circuit breakers of a panelboard.
- On the other hand, panelboards should have a capacity of at least the ampacity of its main wires, which were sized for the calculated load [sec. 480.30]. For example, if the calculated load of the feeder was 153 A, and the ampacity of the chosen wires was 200 A THW (since 153 A * 1.25 = 191.25 A and the next THW size has 200 A ampacity), then the panel must be at least 200-A rated.
- Furthermore, the main breaker must not exceed the capacity of the panelboard [sec. 480.36]. For example, we can't use a 250-A main breaker on a 225-A panel, but we can use a 200-A or 225-A main breaker.
In case I'm correct, I've just answered my own question. But I'm asking for you to check if I'm correct. Thanks in advance!