Violation that is!
I wanted to see if some of you familiar with code could help me out? A swimming pool construction permit was obtained from the county which requires electrical work to be done by a licensed contractor. A plumber installed the electrical and was not the licensed person listed on the affidavit as the one doing the work. There are at least a few code violations I am aware of but want some help with the actual code numbers that would pertain to the various violations.
There is a subpanel on a basement wall feeding a Hayward Omnipl control. The service needs to be 120/240 @ 100 amps, will be in rigid PVC conduit for a distance of 40 feet from subpanel to pool controller. The subpanel is a 4 wire panel with 125A service.
The issues I know of (and there may be more) are:
Type NM -B cable was used (I am told that can't be used as a swimming pool feeder)
The cable contains three 6 awg wires and one 10 awg ground connected to a 100 amp breaker (need #3 copper or larger)
None of the breakers in the subpanel or control panel are labeled/identified
There are no ground fault breakers installed for the pool equipment which are connected to filter pump, booster pump, blower, heat pump, salt cell generator and ac outlet on side of control box.
One of the clamps securing the PVC is not attached because the PVC is not flush with the wall where it comes out of the subpanel.
Paper wrapped around the ground at the subpanel is not trimmed short. (although an easy fix)
Do any of you know the specific code numbers for any/all of the items listed above? Or do any of you see other issues from the photos?
If I misused terminology, please excuse since this is not my area of expertise. Photos below.
I wanted to see if some of you familiar with code could help me out? A swimming pool construction permit was obtained from the county which requires electrical work to be done by a licensed contractor. A plumber installed the electrical and was not the licensed person listed on the affidavit as the one doing the work. There are at least a few code violations I am aware of but want some help with the actual code numbers that would pertain to the various violations.
There is a subpanel on a basement wall feeding a Hayward Omnipl control. The service needs to be 120/240 @ 100 amps, will be in rigid PVC conduit for a distance of 40 feet from subpanel to pool controller. The subpanel is a 4 wire panel with 125A service.
The issues I know of (and there may be more) are:
Type NM -B cable was used (I am told that can't be used as a swimming pool feeder)
The cable contains three 6 awg wires and one 10 awg ground connected to a 100 amp breaker (need #3 copper or larger)
None of the breakers in the subpanel or control panel are labeled/identified
There are no ground fault breakers installed for the pool equipment which are connected to filter pump, booster pump, blower, heat pump, salt cell generator and ac outlet on side of control box.
One of the clamps securing the PVC is not attached because the PVC is not flush with the wall where it comes out of the subpanel.
Paper wrapped around the ground at the subpanel is not trimmed short. (although an easy fix)
Do any of you know the specific code numbers for any/all of the items listed above? Or do any of you see other issues from the photos?
If I misused terminology, please excuse since this is not my area of expertise. Photos below.