Can you please tell me if my voltage drop calculation is correct?
If not correct, can you please explain how to correct?
Panel to 5 gang switch box is 40 feet. 20 amp circuit 12/2 wire.
All lights…
120v – 2.765% = 116.6820 (actual)
Thanks very much!!!!
If not correct, can you please explain how to correct?
Panel to 5 gang switch box is 40 feet. 20 amp circuit 12/2 wire.
All lights…
- Leg 1 from switch is 80’ with 1 amp load
- Leg 2 from switch is 80’ with 5 amp load
- Leg 3 from switch is 20’ with .25 amp load
- Leg 4 from switch is 40’ with .5 amp load
- Leg 5 from switch is 40’ with .5 amp load
- Leg 1: 40’ + 80’ = 120’ at 1 amp = .38 drop
- Leg 2: 40’ + 80’ = 120’ at 5 amps = 1.91 drop
- Leg 3: 40’ + 20’ = 60’ at .25 amps = .095
- Leg 4: 40’ + 40’ = 80’ at .5 amps = .19
- Leg 5: 40’ + 40’ = 80’ at .5 amps = .19
- Total = 2.765 volt drop
120v – 2.765% = 116.6820 (actual)
Thanks very much!!!!