Eddy Current
Senior Member
I was wondering if there is a mathematical way of figuring the amount of breakers and if that will give the the amperage of the overall panel/main breaker?
I was wondering if there is a mathematical way of figuring the amount of breakers and if that will give the the amperage of the overall panel/main breaker?
:? we are not discussing anything that can be measured with a voltage meter:?Okay, I got it; however, can it be check with a voltage meter? If it can, then how does one do it? Please advise?
You would have to count them.What if the panel amperage is unknown is there a way to figure it out with how many breakers there are?
You would have to count them.
You either calcualte the load or measure the load. The only way to know it is to measure.
What if the panel amperage is unknown is there a way to figure it out with how many breakers there are?
And then you know a little more than you did before you counted them,to be specific, the number of breakers in the panel, but little else.And then?
Easy way with main breaker panels is to look at the main breaker. Even if bus can handle more the main is still the limiting factor.If the question is: How much current is presently flowing through the panel, then a current probe/meter will give you an answer, but the reading will change minute by minute, day to night and summer to winter.
If the question is: What is the continuous rated current of the panel, then somewhere in the fine print on the panel label it's listed.
My wife has 12 pairs of shoes. How big is her closet?
If the question is: How much current is presently flowing through the panel, then a current probe/meter will give you an answer, but the reading will change minute by minute, day to night and summer to winter.
If the question is: What is the continuous rated current of the panel, then somewhere in the fine print on the panel label it's listed.
I think you are trying to figure it the wrong way. You can easily have sum of branch breakers total well above the capacity of the panel. Majorrity of the time not all loads run continuously, not all loads run simultaneously, not all breakers are loaded to their maximum rating. The panel has a fixed rating it can handle. Common bus sizes are usually 125, 225, 400, 600, 800 ... Any size in between is limited only because of a main breaker whose setting falls in between.The question was a hypothetical, i was trying to remember if there would be a rating on the panel how do they come up with those ratings?