Can you use a #10 wire in a 15a breaker?
Cartoon1
Florida
Electrical Engineer
Hi all. I'm having voltage drop issues with a equipment that requires a 15ocpd, this equipment is far and I'm trying to increase the cable size to #10 to compensate for voltage drop. Is there any issues with running a #10 wire in a 15a breaker? Fitment wise and terminations.
Thank you
Thank you
Nope. As long as the lugs are rated for #10 at both ends. And if not just splice #12 to it.