Hi,
I understand that this is mostly an NEC based forum but I was wondering if someone could help here. I'm trying to understand how the circuiting works for a small medical clinic. The relevant associated standard is shown below, I have circled the relevant section for the application I have in mind :
What I don't get is the number of branch circuits per patient care locations (1.5). The note at the bottom states one dedicated and one shared between to locations?
Scenario:
So lets assume we have two patient care areas, room X and room Y. Each of these rooms have 5 receptacles each. So if my interpretation is correct one of the receptacles in each room has to be on a dedicated circuit while the rest can be shared between the two rooms, meaning a circuit with two receptacles (one from X and one from Y) ? Is this correct?
X1&Y1 - one circuit
X2&Y2 - one circuit
X3 - dedicated
Y3- dedicated
X4&Y4 - one circuit
X5&Y-5 - one circuit
So in total I would need 6 circuits for 10 receptacles? Is this a correct interpretation or did I get it completely wrong?:?
Lets assume for argument sake that the loads are very small.
I understand that this is mostly an NEC based forum but I was wondering if someone could help here. I'm trying to understand how the circuiting works for a small medical clinic. The relevant associated standard is shown below, I have circled the relevant section for the application I have in mind :
What I don't get is the number of branch circuits per patient care locations (1.5). The note at the bottom states one dedicated and one shared between to locations?
Scenario:
So lets assume we have two patient care areas, room X and room Y. Each of these rooms have 5 receptacles each. So if my interpretation is correct one of the receptacles in each room has to be on a dedicated circuit while the rest can be shared between the two rooms, meaning a circuit with two receptacles (one from X and one from Y) ? Is this correct?
X1&Y1 - one circuit
X2&Y2 - one circuit
X3 - dedicated
Y3- dedicated
X4&Y4 - one circuit
X5&Y-5 - one circuit
So in total I would need 6 circuits for 10 receptacles? Is this a correct interpretation or did I get it completely wrong?:?
Lets assume for argument sake that the loads are very small.