Re: Cannot use #10 on a 35 amp breaker?
Originally posted by twada:
Why does Table 310-16 indicates that the ampacity of #10 is 35amp, and cannot use this on a 35amp breaker?
310.16 rates 10 AWG copper 40 amps at 90C and 35 amps at 75C because that is the rating of the wire.
240.4(D) is a separate issue that requires 30 amp overcurent protection for 10 AWG in most instances.
There are times where you may use 10 AWG for greater loads then 30 amps, look at Table 240.4(G) Specific Conductor Applications for when we can do this, as has been said motor loads are one of the time you may have a breaker larger than 30 amps on 10 awg.
And as Don pointed out you may use the 90(C) rating of 40 amps for derating purposes.