champion
Member
- Location
- St. Louis Missouri, US
I am providing 120vAC power to a 30ft x 30ft canopy located about 200 feet from the front of a car dealership building. The Canopy will have 12 400w metal halide lamp fixtures designed for wet locations. (Huntington series HT2 surface mount units). Each fixture will be 120v AC operated but comes with a ballast quad tap option (120,208,240,277,480). The service is 120/208v 3ph and am unsure about some code requirements for this application.
I have options to provide the power I need and I am undecided as to which would be the best option for safety and design.
Since the lighting load is continuous,I was thinking of providing a 50amp single pole 120v brkr at the main power panel and tapping all lights to this ckt.(400w x 12 x 1.25 / 120 = 50amp overcurrent protection.
---or--- provide a 208v 3ph 4w ckt and connect 4 lignts on each phase lead with a 3 pole 25 or 30amp overcurrent device at the main power panel. 400w x 12 x 1.25 / 208 x 1.732).
Any suggestions would be very much appriciated.
Article 600, sign lighting requires external disconnects located within sight of a sign but this canopy is not really a sign.
Will this ckt require a disconnect located near the canopy?
I have options to provide the power I need and I am undecided as to which would be the best option for safety and design.
Since the lighting load is continuous,I was thinking of providing a 50amp single pole 120v brkr at the main power panel and tapping all lights to this ckt.(400w x 12 x 1.25 / 120 = 50amp overcurrent protection.
---or--- provide a 208v 3ph 4w ckt and connect 4 lignts on each phase lead with a 3 pole 25 or 30amp overcurrent device at the main power panel. 400w x 12 x 1.25 / 208 x 1.732).
Any suggestions would be very much appriciated.
Article 600, sign lighting requires external disconnects located within sight of a sign but this canopy is not really a sign.
Will this ckt require a disconnect located near the canopy?