In a PM, I was asked to look into the methods used to calculate the load, as posted by ramsy and by bob. I have, and I conclude that both methods were wrong. I also believe that a proper load calculation cannot be performed, using the information given.
But first keep in mind that the original question did not ask about service load calculations, and it was not addressed to electricians or engineers.
ramsy said:
Made some changes here: 1? load
20,000 Sq.ft * 3 = 60,000 VA (Tbl.220-3a)
20,000 Sf * 0.75 = 15,000 VA (Table 220-34 Demand Factors for Schools)
--------- Net load = 75,000 / 240 = 312.5 A
Don't do this often. May have missed a few things
I believe you have misinterpreted the intent of Table 220-34 (2002 NEC). That is part of the "Optional Method." You used a "VA/sq.ft." as though it were an amount of load. It is not. It is a threshold for applying a demand factor of 100%, versus 75%, versus 25%. But you have to add up the load separately, before applying the demand factors.
First, you add up all
connected load (Bob missed this point as well). The question did not give us that information. It gave us the connected load for lights and a mysterious category called "mechanical equipment." But it used a rule of thumb, and not actual connected load, for receptacles. Plus it said nothing about a school cafeteria, or a laundry area for employee uniforms, or water heating, or any special equipment for classroom use, or any other possible load. Finally, it did not separate heating from cooling, so we do not get the luxury of disregarding the lesser of the two.
So we have to go with what they did give us. In my first post, I calculated a load (from the information given) of 140,000 VA. Let's call that the "total connected load," for the moment. Applying Table 220-34, we get
- First 60,000 VA at 100% = 60,000
- Next 80,000 at 75% = 60,000
- Total VA = 120,000.