macmikeman
Senior Member
- Location
- Planet macmikeman
I was reading the April 2007 Code article in Electrical Contractor magazine authored by George W. Flach, and this caught my eye. "Where there is 10 feet or more of buried metal water pipe, the grounding-electrode conductor cannot be smaller than 2 AWG copper. Table 250.66 is used to size the grounding-electrode conductor where a metal water pipe is the grounding electrode. In addition, the metal water pipe must be supplemented by one or more of the following: the metal frame of a building, a concrete-encased electrode, ground ring, rod, pipe or plate electrodes." I think this is in error regarding the minimum size of #2. If the largest service conductor is a #2, then the minimum size of the gec per Table 250.66 is #8 copper.