Where does it say that a breaker can only be loaded to 80% I keep hearing that a 20a breaker can only use 16a. All I can find is 210.23(A)(1).
Where does it say that a breaker can only be loaded to 80% I keep hearing that a 20a breaker can only use 16a. All I can find is 210.23(A)(1).
All breakers can be loaded 100% for 179 min 59 sec
Roger
So then a 20a breaker is permissable for a 19a load but why 3 hours? If I had a 15a 4 hour load would the 20a breaker not be ok, ie 15 x 125% = 18.75.
So then what is the specs I have seen that state 100% rated and 80% rated where does this come into play?
Thanks David. That is how I see it, but Ive heard this 80% thing time and again and I was begining to doubt myself. I must have spent an hour in the code book trying to prove myself wrong, and have not been able to. If someone else can show me where it says otherwise please do.Yes, the 20A breaker is OK for a 15A continuous load.
A 20A breaker is permissible for a 20A non-continuous load. A 20A breaker is permissible for a 16A continuous load. A 20A breaker is OK for a 10A continuous and 7.5A non-continuous load on the same circuit, etc.
I'm sure some of the UL experts in the forum could explain this better.
So then a 20a breaker is permissable for a 19a load but why 3 hours? If I had a 15a 4 hour load would the 20a breaker not be ok, ie 15 x 125% = 18.75.
210.20 Overcurrent Protection.
Branch-circuit conductors and equipment shall be protected by overcurrent protective devices that have a rating or setting that complies with 210.20(A) through (D).
(A) Continuous and Noncontinuous Loads. Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the overcurrent device shall not be less than the noncontinuous load plus 125 percent of the continuous load.
Exception: Where the assembly, including the overcurrent devices protecting the branch circuit(s), is listed for operation at 100 percent of its rating, the ampere rating of the overcurrent device shall be permitted to be not less than the sum of the continuous load plus the noncontinuous load.
9.1.2.13 of UL Standard 489
9.1.4.4 of UL Standard 489
100% rated needs cabinet volume and venting, bus, listed for 100% - and conductor 100% rated. It may save $ if bus size and conductor savings etc. are there.
Probably more of a UL issue and in the case of a continuous load.
CIRCUIT BREAKERS, MOLDED-CASE AND
CIRCUIT-BREAKER ENCLOSURES (DIVQ)
USE
This category covers circuit breakers and circuit-breaker enclosures
designed to provide service-entrance, feeder or branch-circuit protection in
accordance with ANSI/NFPA 70, ‘‘National Electrical Code’’ (NEC).
Unless otherwise marked, circuit breakers should not be loaded to exceed
80% of their current rating, where in normal operation the load will continue
for three hours or more.
Continuous Load. A load where the maximum current is
expected to continue for 3 hours or more.
Its a manufacture rating on the most part. Some breakers are rated 100% but many are not.