Capacitive coupling and gfci

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
HYPOTHETICAL QUESTION, IF HAVE SAY 300 FT OF ROMEX 12-2 WG, AND I HAVE 300 FT 12-2 NO EGC, AT THE END OF EACH RUN I HAVE A GFCI, CAPACITIVE COUPLING CAN MAKE THE GFCI TRIP WITH THE EGC, BUT NOT THE ONE WITH NO EGC . ????????????????????????????????????????????????????????????
 
see the UF thread
wg has about 10 nF per 250 ft, no EGC negligible path for leakage current if against wood in air.

higher if buried, on concrete, or grounded metal. Either way, unburied against wood not enough to trip.
 
If the GFCI is at the end of the run, as per the OP, the amount of capacitive coupling on its line side should not be an issue.
 
see the UF thread
wg has about 10 nF per 250 ft, no EGC negligible path for leakage current if against wood in air.

higher if buried, on concrete, or grounded metal. Either way, unburied against wood not enough to trip.
GFCI at start of run. sorry.
 
Some GFCI mfrs state a maximum circuit length. IIRC, Square D says 250ft.

Some references:
 
Some GFCI mfrs state a maximum circuit length. IIRC, Square D says 250ft.
Perhaps this is because a 250 ft. length would not be enough to cause it to trip by itself, but it would begin to reduce the amount of leakage current required for it to trip (say by some noticeable amount such as 10%). But it would take a 2500 ft. length that had 35.4 pF / ft. to cause 4 mA of leakage at 60 Hz, which then could trip a GFCI by itself.
 