HYPOTHETICAL QUESTION, IF HAVE SAY 300 FT OF ROMEX 12-2 WG, AND I HAVE 300 FT 12-2 NO EGC, AT THE END OF EACH RUN I HAVE A GFCI, CAPACITIVE COUPLING CAN MAKE THE GFCI TRIP WITH THE EGC, BUT NOT THE ONE WITH NO EGC . ????????????????????????????????????????????????????????????
 

junkhound

Senior Member
Location
Renton, WA
Occupation
EE, power electronics specialty
see the UF thread
wg has about 10 nF per 250 ft, no EGC negligible path for leakage current if against wood in air.

higher if buried, on concrete, or grounded metal. Either way, unburied against wood not enough to trip.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
If the GFCI is at the end of the run, as per the OP, the amount of capacitive coupling on its line side should not be an issue.
 

domnic

Senior Member
Occupation
Electrical Contractor
see the UF thread
wg has about 10 nF per 250 ft, no EGC negligible path for leakage current if against wood in air.

higher if buried, on concrete, or grounded metal. Either way, unburied against wood not enough to trip.
GFCI at start of run. sorry.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Some GFCI mfrs state a maximum circuit length. IIRC, Square D says 250ft.

Some references:
 

synchro

Senior Member
Location
Chicago, IL
Occupation
EE
Some GFCI mfrs state a maximum circuit length. IIRC, Square D says 250ft.
Perhaps this is because a 250 ft. length would not be enough to cause it to trip by itself, but it would begin to reduce the amount of leakage current required for it to trip (say by some noticeable amount such as 10%). But it would take a 2500 ft. length that had 35.4 pF / ft. to cause 4 mA of leakage at 60 Hz, which then could trip a GFCI by itself.
 