Capacitive Prox Switches CID2

Status
Not open for further replies.
Location
Ohio
Occupation
Engineer
I would like to get some information regarding capacitive prox switches in CID2. I can only find these in standard version, and in intrinsically safe version.

When electronics only have CID1 alternate protection methods (IS, Explosion-proof) this instantly triggers in me the thought that they do not have lesser CID2 protection method variants because they do not have to. Solenoid banks are a good example of this.

Ideally, I want to either move them out of the hazardous area, or find them labelled from the manufacturer CID2. I hate over-designing for CID2. I think the intent of the NEC is to not overdesign CID2 areas.

Here is the capacitive prox switch...
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
See Section 501.105(B)(2). Read it in the context of the main text in 501.105(B). Basically, a device that is current interrupting in Division 2, must have a protection technique suitable for Division 1.
 