Be_O_Be
Member
- Location
- Campbell,Ohio
I'm new to posting here so please bear with me.
I'm dealing with a capacitor bank that serves a freezer warehouse approx. 100k sq.ft. When operating the PF is perfect. The cap bank fuses originally installed were 30amp and would occasionally pop on a single phase. Over time these fuses have been increased to 50amps, can't get a clear answer on who made this decision but this has resulted in (2) different trips by the fire dept. over a two year period..The over sized fuses are overheating and arcing. 50 amp fuses are not the solution.
I will be going back to the original configuration, 30 amp fuses.
The customer & I both understand the value of the cap bank but the question that I can't answer clearly to the customer is "what causes the fuse to trip".
I'm dealing with a capacitor bank that serves a freezer warehouse approx. 100k sq.ft. When operating the PF is perfect. The cap bank fuses originally installed were 30amp and would occasionally pop on a single phase. Over time these fuses have been increased to 50amps, can't get a clear answer on who made this decision but this has resulted in (2) different trips by the fire dept. over a two year period..The over sized fuses are overheating and arcing. 50 amp fuses are not the solution.
I will be going back to the original configuration, 30 amp fuses.
The customer & I both understand the value of the cap bank but the question that I can't answer clearly to the customer is "what causes the fuse to trip".