V vic y New member Location mass. Nov 15, 2006 #1 Who can tell me, if you have an existing 60 kva capacitor bank serving 2 large a/c units and 1 of those units are removed can you simply change the bank to a 30 kva?
Who can tell me, if you have an existing 60 kva capacitor bank serving 2 large a/c units and 1 of those units are removed can you simply change the bank to a 30 kva?
R RayS Senior Member Location Cincinnati Nov 15, 2006 #3 you would need a bank made up of 6 (not 3) or some multiple thereof so you can cut it evenly in half.
you would need a bank made up of 6 (not 3) or some multiple thereof so you can cut it evenly in half.