stew
Senior Member
- Location
- federal way,washington
Have been asked to qoute on an installation of some fairly large cap banks. The total kvar is 400 and the consultant has recommended 2 ea 200 kvar units to accomplish this. The resultant current is 481 ampsx1.35 for a total of 650 amperes according to his numbers. He is asking for parallel 500 mcms for this and I think 400 mcm is sufficient. The other question is code related as it applies to the disconnecting means. Code state s that all the ungrounded conductors shall be simultaneously disconnected which stands to reason. This unit is to be fed from a Square D DS206E breaker in the main swithcgear(800A) set at thier reccomended long time pick up of 560 amps. Is it ok to have the discconect be the breaker.? It is located about 15 ft away on the same side of the gear as the cap bank location . Also does 560 amps sound correct??? The consultant is also specking rsc as the conduit. Is there any reason it needs to be rsc instead of emt? It also seems to me that if I bring the main conductors into a gutter or cabinet above the cap units that I could then slpice in that enclosure and feed each individual unit with a single 400 mcm conductor correct?
[ June 01, 2005, 12:43 AM: Message edited by: stew ]