Currently we have a PFC capacitor manually controlled twice daily with a disconnect switch. 100KVAR , 200A switch, 200 amp fuses, 480V. This meets 460.8(A)(1),(2) & (3) plus the mfgs minimum.
By the looks of the knife blades I would like to put a contactor ahead of this unit. How do I size the contactor? The manufacturer recommends 169% of rated current for the disconnecting means while NEC says 135%.
A contactor is not what I would normally consider a disconnecting means but this is the closest I have found in the NEC for sizing.
By the looks of the knife blades I would like to put a contactor ahead of this unit. How do I size the contactor? The manufacturer recommends 169% of rated current for the disconnecting means while NEC says 135%.
A contactor is not what I would normally consider a disconnecting means but this is the closest I have found in the NEC for sizing.