Capacitor contoller

Status
Not open for further replies.
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Currently we have a PFC capacitor manually controlled twice daily with a disconnect switch. 100KVAR , 200A switch, 200 amp fuses, 480V. This meets 460.8(A)(1),(2) & (3) plus the mfgs minimum.

By the looks of the knife blades I would like to put a contactor ahead of this unit. How do I size the contactor? The manufacturer recommends 169% of rated current for the disconnecting means while NEC says 135%.

A contactor is not what I would normally consider a disconnecting means but this is the closest I have found in the NEC for sizing.
 
Capacitor switching for a standard contactor is the worst thing possible.The voltage and current are phase displaced by 90 degrees and the current arc has a hard time extinguishing.This creates excessive heat and quickly corrodes the standard contact surface.Either purchase a contactor specially designed for cap switching (ie.K/M-contactor) or upgrade the standard contactor to at least 150-175%.:)
 
ptonsparky said:
Currently we have a PFC capacitor manually controlled twice daily with a disconnect switch. 100KVAR , 200A switch, 200 amp fuses, 480V. This meets 460.8(A)(1),(2) & (3) plus the mfgs minimum.

By the looks of the knife blades I would like to put a contactor ahead of this unit. How do I size the contactor? The manufacturer recommends 169% of rated current for the disconnecting means while NEC says 135%.

A contactor is not what I would normally consider a disconnecting means but this is the closest I have found in the NEC for sizing.

The NEC has nothing in it about sizing contactors for controlling capacitors. It only has information on disconnect switches, fuses, and conductors.
 