100831-2045 EST
Larry:
Why?
What is the % ripple, output voltage, frequency, and configuration of the rectifier for your 1000 to 2000 mfd?
If there is a fixed output filter capacitance and the load resistance is constant, then the % ripple remains constant independent of the output voltage. The output current is proportional to the voltage.
If output current is held constant while output voltage is varied and C is constant, then % ripple voltage changes. Constant current with a change of voltage means the load resistance is changed.
% ripple voltage is determined by frequency, rectifier configuration, and the RC time constant.
Thus, output voltage, allowed % ripple voltage, current, frequency, and rectifier configuration must be defined to determine the value of capacitance.
X microfarads per amp is not sufficient.