Why are capacitors rated for 370 volts if you use it on a 240 volt motor .are these ratting peak to peak if so why ?
We gotta work on this some more. I don't know the why but I know the what.In a roughly tuned series LC circuit the terminal to terminal voltage can be several times the voltage applied to the combination.
In order to most efficiently get a useful phase shift in the current of the start winding the capacitor needs to be sized close to the tuned circuit value at 60Hz. Note that actually tuning the LC to resonance would not be a good thing unless you want the current to be limited only by the R of the winding.
In any case the result is that the capacitor must withstand a voltage higher than 240V.
We gotta work on this some more. I don't know the why but I know the what.
370V capacitors are running caps and limit the current in the starting winding in a permanent split or cap start/cap run motor. They are usually between 5 to 70 mfd.
Starting caps are 120 or 240V and are usually higher mfd, 80 to 1000.
Makes sense. Thank you.The details vary from what I discussed,.....
If I remove the running cap of a cap start/cap run motor or psc motor and wire nut the leads together the amps are going to shoot way up and the starting winding is going to smell really bad and smoke is going to pour out. This I know is true. What is the misconception?370V capacitors are running caps (OK) and limit the current (??) in the starting winding (?) in a permanent split or cap start/cap run (OK) motor
No personal criticism intended, but one of the reasons to look at this site is to see how much misunderstanding exists about how 'electricity actually works', e.g. the (?) even from very experienced folks.
Have taught class sections for PE exam for many years, statements as above helps in understanding some misconceptions students often have. ....
If I remove the running cap of a cap start/cap run motor or psc motor and wire nut the leads together the amps are going to shoot way up and the starting winding is going to smell really bad and smoke is going to pour out. This I know is true. What is the misconception?
Starting cap.The misconception is the current limit 'purpose'. A resistor would be lots cheaper than a cap if the reason was to limit current.
The cap is to provide a phase shift to the start (or cap run) winding so that there is starting
Running cap.(or added running) torque,
Seems this has more to do with the size of the running cap.current limit is incidental with the LC values, and can be HIGHER if the wrong LC values in a resonant or phase shift circuit.
So the current in a starting winding has to be limited either duration or amount, am I correct in saying that?For instance, in a split phase motor with no cap, the start winding is wound with lot higher reactance (much different L/R than the main winding) to provide a phase shift without a cap. If the cent sw or the current relay does not open, the smoke gets let out of those also even though designed for no cap.
If the running cap is not controlling current then what is it doing? It's not providing phase shift, that's what a starting cap does.That was a discussion point made to illustrate the cap is not to limit current, a resistor is NOT a legitimate substitute*, but would be IF the reason were just to limit current.
I have worked on a lot of single phase motors. The only ones I have seen where the starting winding stayed in have running caps.The current does not have to be limited if motor wound differently, but economics of the motor winding say to sell motors competitively the start/caprun winding is lower cost if made of lower gauge wire to take less current.
I have never seen a split phase motor that did not have a starting switch.*in most cases -- could go off an a tangent about lighter wire (higher resistance) on a split phase motor help shift phase on the start winding, but wont complicate things.
If the running cap is not controlling current then what is it doing? It's not providing phase shift, that's what a starting cap does. yes, the run cap is to provide phase shift, thus providing higher running torque. Draw out your vector torque/speed diagrams. The start cap is to give higher sero speed torque.
I have worked on a lot of single phase motors. The only ones I have seen where the starting winding stayed in have running caps. Have never seen cap start only without switch either except in the lab, no economic advantage.
A single phase motor with run cap only will start without having a switch.
I have never seen a split phase motor that did not have a starting switch. Have never seen one of those either except in the lab, no economic advantage
I understand all this. What is under discussion currently is the function of a running capacitor.A 2 phase motor works the same as a 3 phase motor, it produces a rotating magnetic vector in space from the stator.
To make a single phase motor self start you must at least make it a 2 phase motor for a short time. This is accomplished by the various ways that you can find discussed on the Internet.
.
I understand all this. What is under discussion currently is the function of a running capacitor.
We have 440V caps in our shop, 370V is more common though. I don't doubt that a 440V cap is made of tougher stuff than 370V caps.Not all run capacitors for PSC or CSCR single phase motors are 370V. There are also 440V capacitors. My limited understanding of the difference is that the higher rated capacitor has more durable dielectric materials, and therefore can operate at higher voltages. The 440V capacitors, because they are more durable can withstand a bit higher ambient temperatures as well.
.....
If the running cap is not controlling current then what is it doing? It's not providing phase shift, that's what a starting cap does. I have worked on a lot of single phase motors. The only ones I have seen where the starting winding stayed in have running caps.
I have never seen a split phase motor that did not have a starting switch.