iwire said:IF the facility has a poor power factor a capacitor bank can reduce the monthly bills
I think not. There is current flowing into the capacitor when you first turn things on. The impact they have on a building's overall power factor doesn't take effect until they reach an equilibrium state. That takes about the same amount of time as the motor starting cycle.dmanda24 said:wouldn't it also reduce the starting current of motors . . .
I think not here as well. I suspect that even if they did significantly reduce motor starting currents, the cost reduction would be no more than pennies per year.dmanda24 said:wouldn't it also . . . reduce costs?
roger62 said:Will a capacitor installed at the meter reduce electrical energy usage of a facility?
charlie b said:Not so, says I.
The amount of energy you use includes energy consumed as real power and energy consumed as reactive power. It is a matter of local utility rules as to whether the customer gets charged separately for the two. But if the power factor is low, you are consuming more energy than you would with a higher power factor, and a capacitor can lower the energy consumption.
charlie b said:The amount of energy you use includes energy consumed as real power and energy consumed as reactive power.