Re: capacitors
Tom,
The typical kW meter only records real(in phase) power. The "apparent power" (the vector sum of the real and reactive power) must still be generated by the power company. The transmission lines, transformers, etc, must be sized to carry this total "apparent power" (the reactive power is never truly used, small amounts are lost to impedance/heat---but it must be initially generated and then carried by circuit conductors to maintain, for example, the magnetic field in a motor). Power factor correction capacitors at the motor or service localize this circulating reactive current, so that the poco distribution system doesn't constantly carry it. The poco charges users with poor power factor for the oversizing needed to produce, distribute, and carry this additional reactive current --- the KVAR charge. This can be metered via kVAR meter or can be assigned/estimated. A rather complex billing system ensues when combined with other utility charges for demand and load factors. This can amount to big dollars(I've heard of up to 10,000 percent penalties, mostly due to the demand factor!) when starting large AC motors "across the line", or running motors at certain "peak demand periods". Hence the use of power factor correction capacitors and also the attractiveness of AC drives and soft starts (and older reduced voltage starters, etc.) for large motors.
Len
[ March 04, 2003, 08:24 AM: Message edited by: Len_B ]