What is the rated capicity for a 25" run of # 4 ga
stranded wire in amps ?
stranded wire in amps ?
Originally posted by iwire:
4 AWG copper not more than 3 current carrying together is rated 70 amps at 60C, 85 amps at 75C, and 95 amps at 90C.
I doubt highly that your equipment is rated 90C so forget that.
It will be either 60C or 75C rated wire or terminals, you have to go with the lowest temperature rating of either the wire or terminals.
Most times that is 100% correct, however if the termination is marked 75C you can base your ampacity at that higher temp.The # 4 cu wire is sized based on the termination of 60c table as it is less than 100 amp and smaller than #1
Bob110.14(C)(1) Equipment Provisions. The determination of termination provisions of equipment shall be based on 110.14(C)(1)(a) or (C)(1)(b). Unless the equipment is listed and marked otherwise, conductor ampacities used in determining equipment termination provisions shall be based on Table 310.16 as appropriately modified by 310.15(B)(1) through (6).