Carflex cable through drop ceiling

Status
Not open for further replies.
I am a little confused about drop ceilings. I have a ceilng mounted motorized display screen which I had planned to run carflex cable from the screen through the ceiling and to a Jbox above the ceiling. Is this allowed and can someone refer me to the code?
 
Let me help out some of our other readers.
Carlex Cable is not a actual product.
Carlex is a common name for LTNM conduit, its a chapter 3 wiring method.
Cable is typically 2 or more conductors in insulation. Cable may or may not be a chapter 3 wiring method.
What is not a chapter 3 wiring method is portable cord, such as SO, or SJO. This type of cable is never allowed above a ceiling or concealed in walls. See 400.7 and 400.8
The code requires a suitable wiring method, I call it a chapter 3 wiring method.
 