Carlflex unprotected when stubbed up??

Status
Not open for further replies.
Does carlflex have to be protected when coming out of the ground to say a disconnect, box etc..?

356.12(1) says it's not to be used where subject to physical damage, so you might not even be able to use it at all, let alone sleeve it.
 
If you're sleeving it all the way into the box, use EMT or rigid.

EMT doesn't provide protection from physical damage. You would have to use rigid or schedule 80 PVC. If you are sliding the sleeve over the Carflex that is emerging from concrete, you have to solidly fasten the end of the sleeve to the concrete so it doesn't shear off the Carflex if it gets hit hard.

If the Carflex is coming up inside a framed wall, it's already considered protected.
 
subject to damage is up to AHJ interpretation.

Many instances I encounter additional protection for the first foot or two out of the ground is a good idea, above that level the amount of physical abuse often is less but there are still some instances where such protection may need to be higher from grade. Weed whackers, snow removal equipment or other lawn/garden type equipment is often the biggest physical damage threat when a raceway emerges from grade.
 
What would be an example of where this would be a good idea? If the carflex needs physical protection where it enters or exits the ground doesn't that just make the work more difficult?
Placing a U shaped metal cover over it if additional protection is needed where it enters/exits grade may be simpler/less cost then converting it/replacing it to RMC/IMC.

Keeping that in mind RMC/IMC can be buried in as little as 6 inches of cover in some places where the FNMC would need to be under at least 18 inches of cover, so one must look at other aspects to determine what may or may not work and how much one method may cost over another if both methods are acceptable.
 