cat 5 wire with zone sensor

Status
Not open for further replies.

MichaelJ

Member
Location
Georgia
what is the voltage on a Cat5 computer net cable? I have a situation where we stubed up a conduit and a J box and run a 18-3 t/stat wire for a zone sensor for a HVAC system and then the network cable guy decided to run 2 cat5 wires down my conduit, i am having problems with the zone sensor not reading right should be about 1.5 volts @ 70 deg, could the cat 5 wire induce a higher voltage and cause me problems?
 
what is the voltage on a Cat5 computer net cable? I have a situation where we stubed up a conduit and a J box and run a 18-3 t/stat wire for a zone sensor for a HVAC system and then the network cable guy decided to run 2 cat5 wires down my conduit, i am having problems with the zone sensor not reading right should be about 1.5 volts @ 70 deg, could the cat 5 wire induce a higher voltage and cause me problems?
Cat 5 wire should have no Effect on the Zone sensor. Induced currents could effect the data on the cat5. The Cat 5 is twisted which keeps the induced currents very very low, Did the wire get damaged in the pull????
 
It's possible that when he pulled in his CAT5s he "burned" through the jacket and conductor insulation somewhere on your thermostat wire. Disconnect both ends and check the resistance between conductors and then each conductor to ground (the conduit). You should read infinity.

-Hal
 
Status
Not open for further replies.
Top