T tommyh Member Location Colorado Feb 11, 2010 #1 Can I run cat 5 control ckt cable through a 600 volt rated DC disconnect?? It's just a switch control...
Can I run cat 5 control ckt cable through a 600 volt rated DC disconnect?? It's just a switch control...
A/A Fuel GTX Senior Member Location WI & AZ Occupation Electrician Feb 11, 2010 #2 No.....See 300.3 (C). Cat 5 does not have the insulation rating required.
D dbuckley Senior Member Location Canterbury, New Zealand Feb 11, 2010 #3 Unless you get Cat5 cable with the appropriate insulation quality; Clipsal a/k/a Schneider Electric a/k/a Square D make such a Cat5 cable in fetching pink...
Unless you get Cat5 cable with the appropriate insulation quality; Clipsal a/k/a Schneider Electric a/k/a Square D make such a Cat5 cable in fetching pink...
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Feb 11, 2010 #5 What if the CAT-5 was sleeved?
S sameguy Senior Member Location New York Occupation Master Elec./JW retired Feb 12, 2010 #6 Through it like a box or into it and term?